PID Controller Error

This topic contains 3 replies, has 3 voices, and was last updated by  Jegor 1 month ago.

milo milo1996

PID Controller Error

11/09/2017 at 15:47

When I turn on the injection moulder, the PV setting comes up with’HHH’. I can’t find anything in the manual, does anyone have a clue what this means?

All the best

Milo

dedicated
14/09/2017 at 07:30

I bought a crappy PID controller off ebay in a pack (+ thermocouple + ssr). Still can’t calibrate it to work. As I am getting the same ‘hhh’ message, I would be interested in finding that out as well.

Toggle replies
dedicated
14/09/2017 at 13:02

It means the temperature input to the PID is out of range. Check that the setting for the thermocouple type matches the thermocouple you are using (probably type k) and that it’s properly connected. If it’s set to NTC thermistor the thermocouple is effectively a dead short across the input giving a maximum high reading.

Also check the thermocouple for continuity, if it has crimped on spade connectors these can sometimes be bad.

Toggle replies
dedicated
05/10/2017 at 07:15

@milo1996,

Do you have a REX-C100FK02-M*AN by any chance?